This help desk is a free resource intended for discussion purposes only. Neither BOMA, its chapters, affiliates, or Extreme Measures Inc.® are responsible for the information, comments or opinions expressed herein. For complete information, refer to the official publications of the standards themselves.

FAQ & Read-Me Articles
What are as-built drawings / models?
What is CAD and BIM?
How do I resolve an area dispute?
Where can I get measurement standards publications?
BOMA Office Overview
BOMA Industrial Overview
BOMA Retail Overview
BOMA Multi-Unit Residential Overview
BOMA Gross Areas Overview
BOMA Mixed-Use Overview
IPMS for Office Overview
Alternative Methodologies
Glossary of Industry Terms

Building Mechanical Space Allocation

Robert Meder
SCB
March 30, 2016

According to BOMA is it required to include all IGA area in the calculation? For instance, we have 20,000sf of enclosed penthouse mechanical, and our client would only like to include 5,000sf as the building service area. This would take less credit than BOMA indicates we are allowed to take and improve the tenant loss factor. Is this an acceptable approach per BOMA?

David Fingret
Extreme Measures Inc.
March 30, 2016

Hi Robert,

The BOMA 2010 Office Standard requires that all areas withing the IGA are measured and included in the Global Summary of Areas. In order to reduce the organic load factor, you can establish a Market Load Factor by incorporating a Capped Load factor and Capped Rentable Area on a floor-by-floor basis

Thanks,
David

Robert Meder
SCB
March 30, 2016

Thanks David. As using a capped load factor would not correct any building loss issue, it sounds like square footage needs to be removed from the building service, ie not enclosing the penthouse.